stevenal
Electrical
- Aug 20, 2001
- 3,798
All,
I'm looking to specify an 8 MW transformer for connecting two four wire distribution systems that are in phase. This can be accomplished with an auto-connection, but will this be the most cost effective way to go? I know that's commonly the case at transmission voltages, but unsure at the lower voltages.
It will have a deenergized tap changer on the 34.5 side, and an LTC on the 12.47. Power might flow in either direction.
Full system unbalanced loading must be accommodated as discussed in thread238-514665. From that thread it appears the load unbalance might be handled by either a tertiary or a five limb core. Shall I leave that choice to the manufacturer as suggested by davidbeach, or are there other considerations?
Thanks.
I'm looking to specify an 8 MW transformer for connecting two four wire distribution systems that are in phase. This can be accomplished with an auto-connection, but will this be the most cost effective way to go? I know that's commonly the case at transmission voltages, but unsure at the lower voltages.
It will have a deenergized tap changer on the 34.5 side, and an LTC on the 12.47. Power might flow in either direction.
Full system unbalanced loading must be accommodated as discussed in thread238-514665. From that thread it appears the load unbalance might be handled by either a tertiary or a five limb core. Shall I leave that choice to the manufacturer as suggested by davidbeach, or are there other considerations?
Thanks.