Auto Transfer Switch in place of Low Voltage breaker
NickParker
411
Can an Automatic Transfer Switch be used in place of a tie breaker in a Main-Tie-Main with ATS (Auto transfer scheme) for low voltage applications?
There are many varieties of transfer switch available.
One version I have serviced used two molded case breakers with a rear mounted, approved, mechanical interlock and motor operators on the breakers.
Basically an ATS may be designed with any breaker or switch that is capable of non-manual operation.
There are very versatile cable based mechanical interlock devices available.
Ohm's law
Not just a good idea;
It's the LAW!
There are ATS' approved for service entrance duty. That would include fault capability.
If you are seeing an ATS at a lower price it is likely that the ATS under consideration lacks some needed features such as fault interrupting capacity.
Ohm's law
It's the LAW!
There are also ATS that have an integrated panel w/ CBs.
NickParker (Electrical)(OP)26 Aug 24 15:46
'..Can an Automatic Transfer Switch be used in place of a tie breaker in a Main-Tie-Main with ATS (Auto transfer scheme) for low voltage applications?'.
1. Automatic Transfer Switch by definition, it acts like a switch. It does NOT break automatically, on over current during closing or in closed position.
2. On the market, there are ATS* using normal/standard Breakers, with mechanical and electrical interlocked included etc.
Note: a) these normal/standard breakers can be MCBs, ACBs with LSIG.. settings etc.
b) as these are standard breakers, they can have all the features/characteristics of a Breaker; i.e. automatically breaking on over-current while closing or breaks in closed position.
3. The main difference is, ATS does NOT open on over-current while combination of MCB/ACB includes the automatic opening on over current.
4. There could be some cost and size difference. Selection would be based on the application.
Che Kuan Yau (Singapore)
I would go with the main-tie-main and add mechanical interlocks, (if not already present) motor operators and some control circuitry.
Call it an ATS or something else as long as it does the job.
Ohm's law
It's the LAW!
We installed several for station service applications in our generating stations over the last 5 years. All of them were basically switched molded case breaker type, and several were service entrance rated.