Hi,
In ABB ACH580 VFD drive we have output relay RO3 which I'm using for fault signal.
The relay got contact 25, 26 and 27 terminals. 25 and 26 are NC. 25 and 27 are NO.
I'm using fault(-1) option means inverted fault and they recommend to use NO terminal which is 25 and 27.
Im confused.
My understanding is that I have connected my external fault relay in 25 and 27 NO. The relay is energized normally when I power the VFD. So my NO become closed. And my external relay energized as well. When trip happens internally the internal relay trips and 25 and 27 become open (NO) again. My external relay de-energize.
Correct me if wrong
In ABB ACH580 VFD drive we have output relay RO3 which I'm using for fault signal.
The relay got contact 25, 26 and 27 terminals. 25 and 26 are NC. 25 and 27 are NO.
I'm using fault(-1) option means inverted fault and they recommend to use NO terminal which is 25 and 27.
Im confused.
My understanding is that I have connected my external fault relay in 25 and 27 NO. The relay is energized normally when I power the VFD. So my NO become closed. And my external relay energized as well. When trip happens internally the internal relay trips and 25 and 27 become open (NO) again. My external relay de-energize.