jnims
Electrical
- Sep 11, 2000
- 75
I am evaluating unequal breaker loading in an industrial substation. The substation consists of three power transformers and six switchgear groups. Two groups are directly tied to each power transformer secondary by air insulated bus. Tie buses between groups were created by parallel runs of cable in duct banks or bus duct. For normal conditions, the load splits fairly evenly. However, when one tranformer was out of service for maintenance, The load is unequally shared between the four main breakers left in service. I am trying to create a model and use a load flow to verify the model's accuracy. The software program I am using does not appear to preformance the necessary impedance calculations needed to accurately model paralleled conductors (it does perform ampacity calcs). I have reviewed several IEEE papers about modeling parallel conductors, but the calculations are more than I want to attempt in a spreadsheet (cable runs are four conductors per phase).
Is anyone aware of a software program that calculates these impedances so that I can transfer this data to my load flow program?
Thanks for your help.
Is anyone aware of a software program that calculates these impedances so that I can transfer this data to my load flow program?
Thanks for your help.