I am involved in looking at an existing cast in place floor slab that has had numerous holes cut out of it.
The slab is a 7" concrete structural slab spanning between walls and it sits on 6" of void form. Below the void form is sand. We do have drawings of the other areas of the shopping center but not in this particular location.
I was called down the other day to look at an L-shaped opening that the plumber had cut into the floor slab. The contractor realized it was a structural slab and called us in to look at it. (He was assuming it was a slab on grade based on the other visible areas that had obviously been cut out in the past to install other plumbing).. Some years ago another plumber had cut out large diameter circles from the slab, done his piping and then in-filled it with a 4" slab, ignorning the rebar that was cut.
I came up with a detail to restore the capacity at the new opening in which the slab at the opening is chipped back to expose a min. of 8 inches of the existing slab steel. (It appears to be a two way slab with 5/8" bars @ 8" o/c e.w. bottom) Then a full-strength tension splice is made between the existing steel at each end with new bars using a flat plate and double flare groove welds.
Now, this recent opening is a result of a large renovation that is underway to an existing dental office. the shopping center is concerned about the other areas of the floor that had been cut in the past and they want our recommendations on what to do. The last thing we want to do is further disrupt the tenant and tear up the whole floor area, it would effectively shut down their operation.
Any ideas on what to do?
Maybe we can pour some local footings under the slab?
PS-The soil below the slab should be fairly stable since there are basements on either side of this main floor slab.
The slab is a 7" concrete structural slab spanning between walls and it sits on 6" of void form. Below the void form is sand. We do have drawings of the other areas of the shopping center but not in this particular location.
I was called down the other day to look at an L-shaped opening that the plumber had cut into the floor slab. The contractor realized it was a structural slab and called us in to look at it. (He was assuming it was a slab on grade based on the other visible areas that had obviously been cut out in the past to install other plumbing).. Some years ago another plumber had cut out large diameter circles from the slab, done his piping and then in-filled it with a 4" slab, ignorning the rebar that was cut.
I came up with a detail to restore the capacity at the new opening in which the slab at the opening is chipped back to expose a min. of 8 inches of the existing slab steel. (It appears to be a two way slab with 5/8" bars @ 8" o/c e.w. bottom) Then a full-strength tension splice is made between the existing steel at each end with new bars using a flat plate and double flare groove welds.
Now, this recent opening is a result of a large renovation that is underway to an existing dental office. the shopping center is concerned about the other areas of the floor that had been cut in the past and they want our recommendations on what to do. The last thing we want to do is further disrupt the tenant and tear up the whole floor area, it would effectively shut down their operation.
Any ideas on what to do?
Maybe we can pour some local footings under the slab?
PS-The soil below the slab should be fairly stable since there are basements on either side of this main floor slab.