Kbradio
Electrical
- Oct 29, 2003
- 14
Have a 60 conductor 14 AWG cable going out 300' in 1.5" plastibond conduit to level switches, open/closed valve position switches and pressure switches out in a tank farm. While performing a monthly interlock check found that the inputs to the DeltaV DI card never changed state from "1" to "0". The input wires have 60 volts of induced voltage. Every 20' of the plastibond conduit we tied the sections to ground and the voltage came down by 4 volts for evey ground added. Now the induced voltage is down to 32V AC which is under the "off" threshold (34V AC) of the input to the DI.
We are grasping at straws here to rectify this problem. Now in the process of putting snubbers 1uF cap in series with a 100 ohm resistor to put a 2500 ohms AC load to ground to discharge this induced voltage.
Anybody have any ideas on this? Thanks Frank.....
We are grasping at straws here to rectify this problem. Now in the process of putting snubbers 1uF cap in series with a 100 ohm resistor to put a 2500 ohms AC load to ground to discharge this induced voltage.
Anybody have any ideas on this? Thanks Frank.....