I recently ran into a client grounding scheme that I'm not too familiar with. I could use some insight from the group.
For instrumentation (pressure transmitters, for example) and communication (serial coms), they connect the sheilds to a cabinet ground buss labled "IE" which I'm assuming is Instrument earth. Equipment grounds are taken to another cabinet ground buss labled "PE" which is protective earth.
This is a very common practice which I'm use to seeing.
However, instead of separate ground cables connecting both busses to external customer PE and IE grounding points, only a PE ground is run. A .01uF is connected between PE and IE in the control cabinet. This is the practice I'm not use to seeing. What are the advantages/disadvantages to this configuration.
Also, I'm told that the individual serial com shield were passed through separate .01uF caps to PE before a single cap was used for all connections from IE to PE. Wondering if this practice was only intended for serial communication and possibly extended (by error) to all instrument grounds.
Your comments are greatly appricated.
For instrumentation (pressure transmitters, for example) and communication (serial coms), they connect the sheilds to a cabinet ground buss labled "IE" which I'm assuming is Instrument earth. Equipment grounds are taken to another cabinet ground buss labled "PE" which is protective earth.
This is a very common practice which I'm use to seeing.
However, instead of separate ground cables connecting both busses to external customer PE and IE grounding points, only a PE ground is run. A .01uF is connected between PE and IE in the control cabinet. This is the practice I'm not use to seeing. What are the advantages/disadvantages to this configuration.
Also, I'm told that the individual serial com shield were passed through separate .01uF caps to PE before a single cap was used for all connections from IE to PE. Wondering if this practice was only intended for serial communication and possibly extended (by error) to all instrument grounds.
Your comments are greatly appricated.