Recent content by baaman

  1. baaman

    1+ pad mount transformer

    East to West, same phase. Thank you, Bob
  2. baaman

    1+ pad mount transformer

    Can we feed a 1Ø pad mount transformer, from 2 different directions? It is the same phase both directions. Thank you, Bob
  3. baaman

    Lightning Arresters

    We use a bracket for both 3 phase and 1 phase. We are a Cooperative, so we make a circle ground or have 2 points were it is grounded. Thank you, Bob
  4. baaman

    Lightning Arresters

    Thank you, that answers my question. Bob
  5. baaman

    Lightning Arresters

    They are on utility poles, 5 sets per mile. Thank you, Bob
  6. baaman

    Lightning Arresters

    We are getting wrote up for hooking up lightning arresters wrong. The engineer wants the bottom to go to the pole ground. All 3 straight to pole ground. The old way was to hook 3 together, than take each one to the system neutral. What are your thoughts. Thank you, Bob
  7. baaman

    eddy currents

    Thank you, that answered my question. Bob
  8. baaman

    eddy currents

    We are upgrading a old service, OH to URD. New service is 2 phase 14.4 in a fiberglass transcloser. Primary URD is in 2 pipes,schedule 80 pvc. Transformers are on a concrete pad, 6" with rebar. Will we have trouble with eddy currents, because of the rebar in the concrete? Thank you, Bob
  9. baaman

    Arc on transformer bank

    Thank you, waross. Bob
  10. baaman

    Arc on transformer bank

    Temp. connection. 2 hot line clamps on #6 copper wire. One clamp on the floating high side, other clamp on the copper for the tank grounds. Thank you, Bob
  11. baaman

    Arc on transformer bank

    Meterman and ape. changed a 480 volt meter at a water well. It is a 3 Ø 240/480 center grounded delta on the low side. High side is 14,400. Lineman grounded the high side before opening the cutouts. My question is when they closed the fuses in, they closed the 2 outside fuses in first. The...
  12. baaman

    Fault Indicator

    Question was, why did the indicators not work. When they disconnected the regulator the OCR stayed in. That makes it a bad regulator. I did find out why they did not work.I will answer nice storys questions, no ,yes, we did not know the fault current at the time of the outage. After getting with...
  13. baaman

    Fault Indicator

    We had a bad regulator on a primary line. Voltage is 7.2, the fault indicators did not work. The indicators are Linam 100 amp trip, made by Chance. The lineman put the indicators on both sides of the regulator, showed white. Disconnected regulator, tried the OCR, and it closed right in and held...
  14. baaman

    Wrong voltage on 167 KVA bank.

    When I went back they had the transformers changed out. The transformers they took down, I could not find. On the dock, with other transformers. Thank you for all the help. Bob
  15. baaman

    Wrong voltage on 167 KVA bank.

    Thanks for the help, I had to stay in today. Tomorrow I will go out and see what we can do. I will let you know. Bob