Thanks everyone for your valuable comments. No code allow us to take the make-up air from car park to the Dishwasher area. The possibility of considering scrubber chemical filter is a very expensive option and may not be acceptable to the authorities. So I am not considering this option anymore.
@HVAC-Novice: Being a professional engineer, I still come across few challenges where I need expert opinion from other professionals who already came across such case study and successfully resolved it. Here we are only discussing about fresh air intake but not exhaust.
In our current project, We have no option left to take make-up air for the dishwasher area except from basement carpark but due to the toxic chemicals (carbon monoxide) contained in vehicle exhaust system, we cannot directly take make-up air. I would like to know if there is any possibility to...
Thanks, everybody for your valuable comments. I do agree with energy professional to use silencers without any media. Therefore, I would also prefer selecting the attenuators that do not contain any media to avoid grease-related accumulations. Rather, such silencers rely on tuned chambers that...
In my current kitchen ventilation design, I did not propose any sound attenuators on the ecology units' exhaust ductwork because grease is present in the exhaust air, this grease can build up in the sound attenuators and cause a fire hazard. In this situation, a different noise mitigation...
See attached spiral slide cooling load calculation. Any comments/corrections would be highly appreciated.https://files.engineering.com/getfile.aspx?folder=8e259555-1c82-4315-a5df-bdfe22112f68&file=Spiral_slide_cooling_load.pdf
A metallic spiral slide (see attachment) is being constructed in the water park where children can play in the slide which is located in the water feature pond. This park is located in Dubai where ambient conditions are extremely hot and humid in the summer. To prevent hot metallic surfaces to...
I am calculating the stormwater holding tank capacity for a large park. I need help in considering the run-off coefficient in this case. The stormwater after percolating the soft scape/soil will enter into a perforated piping network which is provided below the soil layer. Eventually, all this...
Few suggestions below..
Optimization of central extract ventilation system design for dirty areas such as wash rooms, pantries, etc.
Design considerations in mission critical cooling circuits
ACMV design attributes of extra tall high volume spaces
Optimization of fire protection system...
Pressure break heat exchangers are needed for high rise towers to minimize the casing pressure of chilled water pumps and also pressure rating of chillers, condensers and valves. The maximum pressure rating of chillers and condensers available in the market is up to 20 bar. the pressure rating...
@Danschwind...thanks for your input.
@LittleInch..The chilled water pressure has already increased to 263 psia mainly due to maximum static height of 120 m and fill pressure but standard HVAC components are generally not compatible with such max. pressure rating. So either we need to increase...
@LittleInch thanks for your valuable response. In case if expansion tank cannot be relocated to upper floors, The maximum pressure (P2) will be much higher than required. In my case,
P1 = static height + fill pressure = 185 psia
P2 = P1 + pump head = 185 + 78 = 263 psia
Above 263 psia...