Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by fne

  1. fne

    Pile cap detailing for eccentric loads

    Thank you for the responses. It is a two pile group and the axis of the pile group is the axis of the moment. It is a new column in an addition up against an existing building. One thing I did not take into consideration when posting the original thread is the compressive force in the cap...
  2. fne

    Pile cap detailing for eccentric loads

    CRSI Pile Cap Design Guide, Figure 4.3 shows minimum pile embedment and a distance to the bottom reinforcing in the pile cap. The distance to the reinforcing places it above the top of the pile. If the loading on the cap is eccentric to the pile or pile group, there will be a moment in the...
  3. fne

    Increasing the allowable load on a steel/concrete composite floor system

    If new beams are introduced to an existing composite floor system, how are the design of the new beams and verification of existing handled? How does the introduction of the new non-composite beams affect the existing composite members?
  4. fne

    Open-Web Steel Joist reinforcing - welds

    In the paper "Evaluation and Modification of Open-Web Steel Joists and Joist Girders" (Broekmeier and Fisher), the authors account for the stresses that exist in the members due to dead load if the member is not shored when reinforcing takes place. Yet in their discussions on the welds, in...
  5. fne

    Repair of defects in formed concrete surfaces - accepted standard of practice

    For rough finished formed concrete surfaces, is their an accepted or specified standard on when the defect should be patched? All I could find in ACI 347 was patch the defects and tie holes. They address knocking down the fins greater than 1/2", but nothing on the size of defects that should...
  6. fne

    Roof Live load (Lr) vs. Live Load (L) in ASCE 7 load combinations, cranes supported from roof

    dhengr - I feel we are of the same generation. I look at the size of the first ASCE-7 I owned compared to the latest and ....
  7. fne

    Roof Live load (Lr) vs. Live Load (L) in ASCE 7 load combinations, cranes supported from roof

    waytsh - being an old f**t, I would use ASD, but the young engineer working on it will probably use LRFD. The discussion was whether you could use the load combination which includes 0.75 Live (putting the crane load here) when combined with the snow and other loads. We are aware of the...
  8. fne

    Roof Live load (Lr) vs. Live Load (L) in ASCE 7 load combinations, cranes supported from roof

    To help in understanding question, we are looking at where the crane load should be in the ASCE-7 load combinations.
  9. fne

    Roof Live load (Lr) vs. Live Load (L) in ASCE 7 load combinations, cranes supported from roof

    Existing structure has bridge cranes suspended from the roof structure (joists). In looking at this to evaluate the joists would you consider the crane load a roof live load (Lr) or could it be considered as a live load (L)? Reference also the definitions of the two in the ICC building codes...
  10. fne

    E60 vs E70 welding electrodes

    Our specs for welding structural steel (buildings) have historically called for the use of E70 electrodes. Recently a contractor has requested the use of E60 for some A36 material citing "matching strength criteria". A little research reveals this is not a new concept. What are other firms...
  11. fne

    Identifying old steel joist

    Does anyone recognize this joist? Any available info would be appreciated.
  12. fne

    Electrical wiring rated to withstand 1000 degrees for 15 minutes

    cdafd - thanks for the link, that helps. Does anyone have any experience with a product that would meet these requirements?
  13. fne

    Electrical wiring rated to withstand 1000 degrees for 15 minutes

    Yes, without the reference to NFPA 70. http://files.engineering.com/getfile.aspx?folder=ee868cc9-f748-4ac4-8035-57366e455f20&file=910.PNG
  14. fne

    Electrical wiring rated to withstand 1000 degrees for 15 minutes

    Not sure this is the proper place to post. In Ohio building code there is a section that requires "wiring for operation and control" of some equipment to be protected to withstand 1000 degrees for 15 minutes. Is anyone familiar with a product that would meet this requirement or anyone in Ohio...