Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by gvasiliou

  1. gvasiliou

    SCCR rating - engineering supervision

    Hi guys, interesting topic. Although i would like to ask something about LionelHutz example. I suppose you mean "after installing the breaker". Has the breaker to be a "current-limiting" breaker, being able to effectively limit SC Current...? If breaker is not current-limiting and 22 kA...
  2. gvasiliou

    Power Line Carrier Communication from 11kV to 400V

    http://en.wikipedia.org/wiki/Power_line_communication
  3. gvasiliou

    Two LV bus bars with Transformer Different Phasing / Phase Rotation

    If 132 kV Side is not yet connected to the grid or can be easily isolated you may try this if you like. Isolate both GT3 and GT5 from 132kV grid. Force closure of "interconnector" and GT3 and GT5 breaker. Find a smart way to supply 480V AC to the primary side (132kV) of GT3 or GT5. You should...
  4. gvasiliou

    Black Start Generators Wiring Diagram/s

    Black Start Generators (BSG) are used in power plants to provide the "first" source for the auxiliaries subsystems of bigger engines/turbines to work. For sizing You need to know from customer what is the load/s that Generator is going to get, in how many steps. Also is good to know if the...
  5. gvasiliou

    NEMA MG-1 Clarification

    Generator datasheets refers that manufacturing of generator is according to NEMA MG 1-32. Part 32 of NEMA MG-1, section 32.13, NEMA Refers: Can somebody explain this .... with more details...? I admit is a little confusing term since 3ph short circuit capability of generators is described...
  6. gvasiliou

    Generator Calculations Bug

    After some initial research: High impedance earthing (low current i.e 10A) needs special treatment by protection devices to ensure correct "understanding" of the fault current. For this reason some times low impedance (high current i.e 200Amps) is used, since higher currents can be picked up...
  7. gvasiliou

    Generator Calculations Bug

    OK... If it is like that, this explains why the fault current coming from the generator side is 50% increased versus standalone operation. As well this proves that generator windings are in reality exposed to higher currents from what they can really produce (and most probably withstand). I...
  8. gvasiliou

    Generator Calculations Bug

    Can you explain this a little bit more...I was expecting unfaulted phase windings of the generator to contribute to the faulted phase by a small fault current (calculated using the a operator). I wasn't expect unfaulted windings to carry grid contribution....
  9. gvasiliou

    125V DC circuit breaker

    Hi odlanor, Did you check with Siemens the possibility to replace the trip unit?
  10. gvasiliou

    Generator Calculations Bug

    LOL.... That sounded something like : Apply some impedance to your machine and stop posting questions! (just joking). I'm afraid math is correct. Calculations have been checked even by ETAP. Before to put my hand to my pocket to draw a lot of my company's money for applying neutral impedances...
  11. gvasiliou

    125V DC circuit breaker

    Stupid Question : Since they have 690V-AC Circuit Breaker i assume it is 3 or 4 pole. No matter what is the trip unit, how a 3 pole CB deals with two poles of DC systems...?
  12. gvasiliou

    Generator Calculations Bug

    Waross, for sure grid boosts the fault current using positive and negative sequence contribution , even if zero sequence of the grid is not able to reach the fault location due to the transformer delta. I can even understand the path you describe, if i draw the impedances using symmetrical...
  13. gvasiliou

    Generator Calculations Bug

    Actually we talk about a Stamford Alternator equipped with an AVR (i.e MX321) combined with PMG.
  14. gvasiliou

    Generator Calculations Bug

    Hi david, Actually in my configuration the utility (0) can't reach the fault location due to the existance of delta winding on LV side of the intermediate transformer. As a result, if you try to draw utility only fault circuit (i skipped this from my post) the fault current at LV bus 3 will be...
  15. gvasiliou

    Generator Calculations Bug

    Hi guys, For one more time I need your opinion in a kind of strange issue, which escapes my understanding. Performing a single line to ground short circuit calculations (Low Voltage Side) in a simple Generator power plant using a step up to transformer, we can observe the two following facts...