So, the water issue is not a concern. there is insulated sheathing out the outside face.
The AB comment is related, because there is language in the code about the washer plate being within 1/2in of the wall sheathing for AB's... that was written due to eccentricity concerns in the testing, I...
Is there any reason why putting the shear wall sheathing on the inside face of an exterior wall is not acceptable, or requires additional consideration?
Seems to me that the sheathing nailed to the inside face of the sill plate creates an eccentric loading condition, if the sill is then nailed...
thread507-282970
Hello,
I found the referenced thread, which discusses the pros and cons of wet setting rebar. I have not been able to locate the pertinent code sections under the new codes.... ACI 318-19 and 2022 CBC.
Anyone know where to find this?
Thank you.
Section 12.14.8.1 specifies Fa=1.4 for soil sites, but also allows Fa to be determined by Section 11.4.4 which requires Fa to be a minimum of 1.2 and references back to 12.14.8.1.
As a designer, Ive never used the Simplified approach... as a plan reviewer, I'd like to get clarification.
Any...
Was the requirement to put the lap splice in the middle third of the column removed? ACI 318-19 Section 18.14.
I haven't even found it in the SMF section.
It has been awhile since I looked at one of these.
I never have a major problem with them.
They have always seemed to have a better understanding than the jurisdictions do because, as noted previously, jurisdictions cannot afford an SE. I think a lot of engineers have trouble adjusting their standards because they are used to reviews by ...
I wouldnt detail the exact dimension, and have the contractor verify dimensions and produce shop drawings. Or, I would build tolerance in with a field weld... double L bracket.
RWW0002- Okay. I get that. If Im not mistaken, the truss designers usually assume either direct applied ceiling or they specify a nominal bracing. In the situation you describe, Id recommend bracing the BC either way. A continuous runner is easy and cheap, add some bay blocking and youre there.
RontheRedneck - What software do you use?
And all, is the concern that the truss will fail? Or that you dont have an accurate holdown force to work with?
I'll certainly be adding this requirement and taking a look at this in the future... thanks.
Thanks for the reference. Ive been blocking under each sheathing edge, clipping the blocks together, and coring holes through them to provide equivalent ventilation
Im not convinced a recession is coming... and I urge people not to be convinced ahead of time. If they convince us a recession is coming, it will come.
An old engineer once told me that the staggered edges used in a vertical layout provides better racking resistance. I always figured, if it matters for diaphragm shear.. it matters for shearwall shear. But NDS T 4.3A footnote 2 states the values for shear can be increased...... if ..... the...