Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SDETERS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by Jpascp

  1. J

    Poor Power Factor

    As per ETAP simulations is possible to improve PF with VFD.
  2. J

    Power Outage at Heathrow Airport - Realiability and Resilience

    Any idea that what could happeded? Harmonics issue? No fire resistant concrete walls between power transformers? Sprinkler system was not operational? No redundancy? Others?
  3. J

    Buried Earthing Grid in Concrete Foundations - German Philosophy

    We do not use any copper inside as foundation reinforcement electrode. Normally is used galvanized steel plate since is cheaper as shown in photos. Nowadays in industrial projects is normally also to connect buried main earthing grid to reinforcement foundations. In this way the total impedance...
  4. J

    Buried Earthing Grid in Concrete Foundations - German Philosophy

    Attached file with some photos of buried earthing grid inside concrete foundations.
  5. J

    FEED Stage Deliverable Documents

    For a FEED stage do you know which are the minimum deliverables documents (written, drawings and calculations) needed? Is there any standard/rule for it?
  6. J

    Extra Loop for MV Cables

    Do you usually use in electrical installations extra loop for MV Cables in origin/from and destination/to? I believe that is a good solution in case of an event short circuit at its terminals.
  7. J

    Tolerance for rated short time withstand current in MV switchgears

    Yes, main question is if there are any tolerance by IEC or IEEE. If there are any tolerance nominal values MUST be followed.
  8. J

    Tolerance for rated short time withstand current in MV switchgears

    Hello I have checked with one Vendor and they send me part of tests report and is mentioned values a little bigger than nominal (Ik3" and Ip) ans well related with duration of short circuit in seconds. However in nameplate will be the mominal values (for example Ik3"= 40 kA (3 sec), Ip= 100 kA).
  9. J

    Tolerance for rated short time withstand current in MV switchgears

    I was checking IEC 62271-200 and I did not find anything about short circuit tolerances. For example SIEMENS MV Switchgear 8DA10 (40,5 kV/2500 A) model has 40 kA (3 sec). For some project we get IK3"= 40,66 kA. What is your experience about it?
  10. J

    Synchronous Condensor (SC) or Hybrid Synchronous Condensor (H-SC) for Steel Making Plants (SMP)

    Thanks for your support. Yes in general in SMPs we use VSCs type SVCs or STATCOMs. I have never seen any SC in it. It seems that for grid upgrades yes it is used SCs or H-SCs. I did not find any thing in internet about H-SCs for SMPs.
  11. J

    Synchronous Condensor (SC) or Hybrid Synchronous Condensor (H-SC) for Steel Making Plants (SMP)

    Do you have any data of it? SLD? Some inputs were gave to me that when EAF is working could cause some vibrations in SCs shafts. What I red until now is that 3 VSCs systems: only STATCOM only SC Both SC + STATCOM Are often used in grid voltage stability, mainly in primary substations. For...
  12. J

    Synchronous Condensor (SC) or Hybrid Synchronous Condensor (H-SC) for Steel Making Plants (SMP)

    My question now is directly use this kind of VSC (Voltage Source Compensation) in Meltshops. As anyone knowledge of this kind of systems in SMPs?