    new openings in existing wood-framed walls

    Less than 10% reduction in capacity of lateral resisting elements is the code allowed rule of thumb. However, you have to check overturning forces as well and the hold down implications according to location of openings. Example: If you have a 30' continuous wall, you can likely add a 3'...
  2. kwinner

    Wood Columns...Possible or Bad Idea

    This needs to be a cantilevered diaphragm with wood shear walls, no steel required. R=6.5 no question. Recalculating for R=6.5 you get V(low roof)=2720*(2.5/6.5)= 1046#. Chord Forces T=C=2720*9'/25'= 376#. With omega(2.5), T=C=941#. From the elevation shown, the low roof diaphragm only appears...
  3. kwinner

    Library Floor Deflections

    Not sure what your spans are, but a vibration calculation might be helpful here too.
  4. kwinner

    Ledger board...how to fasten to stone wall

    I agree with pham. I doubt you will find any products rated for use in this condition.
  5. kwinner

    Tread Riser Support

    What is critical when designing these feature stair elements is communicating clearly with the architect and owner on what their desires and expectations are. If this is an artistic feature, and vibrations/stiffness are not of concern, then you can push code limits and help provide the desired...
  6. kwinner

    Hole deformation consideration in bolted connection bearing check

    Where I have seen this specifically referenced is in the Seismic Design Manual Section D.2(a) requiring bolted connections in the SFRS to be designed with deformation as a design consideration.
  7. kwinner

    OMF Continuity Plate Design?

    Sorry, AISC 341-16. "unless you consider this to be the maximum moment that can be transferred to the connection)." That is exactly the case. In Part 4 (Moment Frame Section) it gives a similar list of limiting aspects of the system, including overstrength seismic load (AISC 341-16) or R=1...
  8. kwinner

    OMF Continuity Plate Design?

    While it appears they are trying to discourage this type of design, AISC 341-18 Section 4.2(b) allows for the "overstrength seismic load" to be the limiting design moment for OMF connections. This is similar and replacing the R=1 option from AISC 341-10.
  9. kwinner

    Another Wood Moment Connection Question...

    I would think about using SDS screws to reduce number of fasteners (avoid splitting) and add some compression between the members.
  10. kwinner

    Angles force cause torsional buckling?

    Yes, consider torsion. Refer to AISC 360 Specifications Section H3.1 and H3.2.
  11. kwinner

    A crack in a MAIN BEAM under a house with a hairline crack in it - Is that concerning ?

    I don't think it is a take it or leave it situation. It is a get an engineer to assess it and provide their recommendation as to how to proceed. If they come back with recommendations for 15k of repairs, get another engineer to assess it. Don't just ignore it, but also don't feel backed into...
  12. kwinner

    A crack in a MAIN BEAM under a house with a hairline crack in it - Is that concerning ?

    Yes, sistering on additional framing in a reasonable way would help eliminate any cause for concern, and that would be my recommendation if this were a concern. That should be possible to do without any demo or excavation. They got somebody down there to take the photo, and the work required is...
  13. kwinner

    A crack in a MAIN BEAM under a house with a hairline crack in it - Is that concerning ?

    I quit stressing over issues like this long ago. There are other potential structural deficiencies that I have seen over the years that keep me up at night, and I will not let a not let a single-story, lightly loaded floor beam be a concern. What does a real failure look like in this case...
  14. kwinner

    Interior mezzanine wall sheathing

    I-beam - Just be aware that if you are designing for seismic loads, R=2 for sheetrock walls.
  15. kwinner

    Retrofit Holdown - Can't Use Epoxy

    Not until we get some research and testing done (which I would think would be valuable for Simpson to pursue)