  1. mikelangel78

    Outer Sheath MV cable DC test

    Thank you for your wise advice. Regards
  2. mikelangel78

    Outer Sheath MV cable DC test

    I've been thinking about my own question. Perhaps if I connect the negative terminal (-) of the DC source in the earth and the positive terminal (+) in the cable sheath, and because the electrons flow from the (-) to (+), i'm not be able to detect a defect in the insulation of the cable. Am I...
  3. mikelangel78

    Outer Sheath MV cable DC test

    Hello! I'm performing DC test to verify the outer sheath integrity on a MV 36kV cable after laying, according to IEC 60840 & IEC 60229 standards. I'm using a BAUR testing equipment. According to the manufacter, the test equipment negative (-) terminal should be connected in the outer sheath and...
  4. mikelangel78

    Line Traps + Capacitor Coupling Voltage Transformer

    Thank you very much all of you. A special thanks to scottf. Great file!!
  5. mikelangel78

    Line Traps + Capacitor Coupling Voltage Transformer

    Thank you davidbeach. I think the Line Trap should be a LC low-pass filter to allows the power frequency to enter in the substation, and the CCVT must have a band-pass filter or a high-pass filter, in that case i'm not sure, because the PLC frequencys, I think I've read this somewhere, came in...
  6. mikelangel78

    Line Traps + Capacitor Coupling Voltage Transformer

    Hello, I'm very interested in PLC systems. I have a Line Trap and a Capacitive Coupling Voltage Transformer installed in a 220kV substation. I would like to apply the formulas and get the values that leave me to understand how these system works. Where could I find a good guide to sizing and...
  7. mikelangel78

    Voltage Transformer Testing - Secondary Phase-Angle

    Yes, sorry, you're right...my mistake "0º"
  8. mikelangel78

    Voltage Transformer Testing - Secondary Phase-Angle

    Hello Testing a HV Voltage Transformer, using a OMICRON equipment (that must be connected to earth) I must inject in the primary side a test voltage, and I want to check the phase-angle in the secondary of the VT. Why the phase-angle should be near zero volts? Thank you in advanced
  9. mikelangel78

    VT - Phase Checking

    Hello everyone, I'm testing a 220kV Voltage Transformer with a CPC100 Omicron device. One of the test that i've to perform is the phase checking. I've a three-phase VT of a bank of three single phase VTs. I'll do a primary injection and measure the voltage between phases and neutral in the...
  10. mikelangel78

    CT Secondary Earthing

    Thank you Scottf for your kindness and patiente. And what could cause the "float up" at the seconday winding potential? Could you give pratical or possible examples? Phearps and induction current that appears in one of the seconday cables cause that "float up".
  11. mikelangel78

    CT Secondary Earthing

    Hello again. I would like to understand better this poiny of the secondary of the CT, grounding. ScottyUK (Electrical)5 Mar 15 13:12 The CT secondary circuit forms a closed loop. The loop is connected to earth as a reference at exactly one location. No current flows to earth, it just provides a...
  12. mikelangel78

    CT - Marshallinb Box and Test Terminals

    I agree with you marks1080, and I don't feel confident in perform these tests, but I have to do it, and I don't have nobody in my company to explain me. And studing these the better way I can...
  13. mikelangel78

    CT Testing - Primary Injection and Seconday Core Checking

    Hello, I've uploaded the diagram in order to be more clear in my doubts. CT: 400A/1-1-1-1 Step 1: Injection of 200A in the primary of phase "0" Confirm that in the terminals X1:25/28 of the marshalling box I will have 0,5A What should be the value of the current between X1:25/29? Step 2...
  14. mikelangel78

    CT - Marshallinb Box and Test Terminals

    Hello, Please find attached the diagram were you could see the marshalling box connections. Could you please help understand the function of the PHOENIX SB2-RTK/S and SB4-RTK/S slide bars? After the CT tests are donne, and if all the secondaries of the CT are used, these sliding bars should...
  15. mikelangel78

    CT Testing - Primary Injection and Seconday Core Checking

    Could please someone confirm my bellow conclusion/assumption? Thank you in advanced