  1. recman55

    Tripping Breaker on Wye Delta start

    Thanks for you feed back. It has not tripped today since I matched the two motor loads.
  2. recman55

    Tripping Breaker on Wye Delta start

    I read the thread you referred to, after further investigation it appears the motor is tripping after it has started in the bale compression cycle. ( full motor load) One moter pulls 120 amps the other 190 amps. I turned down te pump pressure, Set it by amps to the same as the other motor amps...
  3. recman55

    Tripping Breaker on Wye Delta start

    I have a two motor Baler with two 75hp 460v 3 ph motors with wye delta start. The motors run two piston hydraulic pumps. One motor is tripping the breaker on start. The breakers are a 125 amp breakers, one for each motor. The loaded amps on both of the breakers are 120 amps. Amps to the six...