recman55
Industrial
- May 10, 2012
- 3
I have a two motor Baler with two 75hp 460v 3 ph motors with wye delta start. The motors run two piston hydraulic pumps. One motor is tripping the breaker on start. The breakers are a 125 amp breakers, one for each motor. The loaded amps on both of the breakers are 120 amps. Amps to the six delta legs are 63 amps.
There have been only two of these balers made. I have found other engineering errors in the equipment. Is the breaker to small for the motor? What is typical breaker sizing for wye delta start curcuits?
There have been only two of these balers made. I have found other engineering errors in the equipment. Is the breaker to small for the motor? What is typical breaker sizing for wye delta start curcuits?