    Slab and wall joints in concrete tank

    In a liquid-filled tank, must construction joints in the wall align with the construction joints in the slab? These are construction joints, not contraction joints--i.e., continuous reinforcement. Specifically, this is for a circular tank, and according to the specs, the slab will be placed in...
  2. rholder98

    Density of Portland Cement?

    Why is portland cement 94 #/cf alone (SG=1.51), but is 197 #/cf (SG=3.15) when used in a mix design?
  3. rholder98

    Construction bracing of CMU walls

    Thank you, hokie. I was feeling like the guy who tells a joke and hears only crickets. That is, in fact, the brace--installed parallel to the wall. You know, because it would just be in the way if they brought it out from the wall. Jokes aside, though, concretemasonry, thank you for the tip...
  4. rholder98

    Construction bracing of CMU walls

    I was a little worried, because I could not find any temporary bracing for these 28 ft cmu walls. Luckily, though, I finally found this. Enjoy. . . .
  5. rholder98

    Batch plant broke down. . .

    Thanks to all for the responses. The bottom line is this tank has to be in use for 50+ years, and has to be watertight. I don't like being the unreasonable engineer, and I always try to work with contractors to resolve issues like these, but this is a big one. What he wants to do might work...
  6. rholder98

    Batch plant broke down. . .

    I think bond would be okay, because the surface is so rough. I could require a bonding agent, as well. The thickened slabs under the walls will act in flexure, but the slab itself won't see much. What really concerns me most is: a)the roughness that gives me the bond could cause cracking in...
  7. rholder98

    Batch plant broke down. . .

    It's very good soil, mostly caliche at this depth. Groundwater is not an issue.
  8. rholder98

    Batch plant broke down. . .

    . . .40 yards into a 200+ yard pour for a section of slab in a carousel aeration basin. Now a large section of the slab has about half the thickness in place, with most of the top mat of steel exposed, and some of the bottom mat exposed. They at least had the quick-thinking to 'spread out'...
  9. rholder98

    Reinforcing Inserts at Construction Joint

    Try Diamond Dowels from PNA Construction Technologies. www.pna-inc.com These are for shear transfer, not tension or moment.
  10. rholder98

    Minimum Reinforcing in Concrete Tanks

    vincentpa, I disagree that 10.5.4 is "quite clear". It says to use the minimum required by 7.12, but again, 7.12.2.2 says to distribute the temperature and shrinkage reinforcement to each face, so I don't think it's telling us to use the entire 0.005 on each face. Take a 12" wall, d=9"...
  11. rholder98

    Minimum Reinforcing in Concrete Tanks

    I think 10.5.1 does apply, because it says "At every section of a flexural member. . .", which, for a tank, includes walls. So (10-3) applies for each face, and not less than 200/fy. Also, it need not be greater than 4/3 that required by analysis, per 10.5.3. However, the reinforcement...
  12. rholder98

    Minimum Reinforcing in Concrete Tanks

    I was of the belief that if you satisfy your flexural requirements, you then compare the total amount of steel to your temp/shrinkage minimum, for the whole section. However, 10.5.4 of 350 seems to suggest that you should have the minimum temp/shrinkage on each face. Now, after re-reading...
  13. rholder98

    horizontal cold joint in one-way slab/joist construction?

    Section 17.5 provides a fairly straightforward analysis method, without having to calculate Q. Specify that the cold joint is roughened to 1/4", and you can get pretty decent capacity using the stirrups you already have there. There is a limit to the available capacity, beyond which you will...
  14. rholder98

    Lintel - Supporting 12" Masonry

    That's what confuses me. Article 1.10.1 says it applies to masonry designed in accordance with section 2.2 or Chapter 5. However, section 2.3.3.4.5 says "Beams shall be designed to meet the deflection requirements of Section 1.10.1." Then in the commentary, it contradicts itself again. So...
  15. rholder98

    Lintel - Supporting 12" Masonry

    ACI 530 requires a maximum deflection of L/600, or 0.3" max, for a beam or lintel supporting masonry. csd72, I'm with you when the span makes that seem impractical, but how do you interpret the code requirement (assuming you are in the US)? I designed one of these almost exactly as Gordy2...