Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations LittleInch on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by SA07

  1. SA07

    Lifetime of Fire trace tubing

    Hi We have Firetrace system installed in our electrical panels since 2017. Some piping are starting to crack. All our electrical rooms are clean, air conditioned. Have any one encounter this issue? Any idea what is the lifetime of the Firetrace tubing? Thanks
  2. SA07

    Turbo alternator tripped by reverse power

    Hi We have 2 turbo alternator exporting to utility grid. One turbo alternator tripped by reverse power and generator breaker opened. From fault recorder, we do not see a big fault or disturbance on the network. Feedback from Utility: they were switching flow of power to another substation. Any...
  3. SA07

    Lightning protection of power plant

    Thank you FacEngrPE for detailed explanation and links
  4. SA07

    Lightning protection of power plant

    Hi We are a power plant. Since construction, lightning rod were installed on the boiler, substation 66 kV, lightning arresters on 66 kV lines and earth cables over 66 kV transmission lines. Over time 2 additional small power plants were constructed. They are not sufficiently protected against...
  5. SA07

    Ultrasound testing of MV/HV equipment

    Hi Does someone has a table showing the acceptable levels of ultrasound when doing this test? Are there any standards for these test e.g. IEC? Thanks
  6. SA07

    Can we operate Emerson Scada system/Server with Siemens PLC 400 ?

    Hi We have a Siemens Scada system, 2 servers, 1 process historian. We intend to renew this part as we are having some issues with 1 server. It was renewed in 2015 and previous system installed in 2007. We have 2 power plants exporting to national grid. We belong to an international group which...
  7. SA07

    Can we replace an AVR Basler 250 with Basler 200?

    Hi There are Basler 250 on 3 hydro plants. We have 1 spare Basler 200 in our store for another turbo-alternator. Can the hydro plant replace their Basler 250 with Basler 200 in case of breakdown?
  8. SA07

    Use of sacrificial metal to protect 55 MVA transformer

    Thank you for your feedback. Our local paint company has recommended zinc rich primer
  9. SA07

    Can we start an ID fan motor 700 kW 690 Vac direct on line?

    3 blocks have been replaced on our VSD 1. Unit 1 is operating with VSD on ID fan Unit 2 is operating with Soft starter on ID fan For info Both units are exporting same MW we have 844 kW on aux transfo unit 1 1306 kW on aux transfo unit 2 VSD ID fan 2 operating at 36.3 Hz consuming 221 kW ID...
  10. SA07

    Use of sacrificial metal to protect 55 MVA transformer

    Hi We have corrosion on our 2 x 55 MVA outdoor transformers. We are located a few km from the sea. We can only maintain the transfo. during 1-2 week during annual shutdown. Has someone used sacrificial metal to protect power transformers?
  11. SA07

    Can we start an ID fan motor 700 kW 690 Vac direct on line?

    In 1 week we must start the plant after annual maintenance. Else we will get penalty from utility company. We export on the grid. If we get a soft starter we can start the plant to avoid penalty. In the long run, we will order a vsd to save energy. Even a second hand soft starter will be helpful.
  12. SA07

    Can we start an ID fan motor 700 kW 690 Vac direct on line?

    Sorry for the mistake. I meant supply directly to 690 Vac 50 Hz and operating at nominal fixed speed and the damper is regulating the flue gas flow.
  13. SA07

    Can we start an ID fan motor 700 kW 690 Vac direct on line?

    One boiler is actually operating with the ID fan supplied through a soft starter. After start up, the motor is supplied through the bypass; so DOL. There is a damper to control the flue gas flow. The boiler is operating well now although with a VSD the kW consumed would be much less. Our normal...