Dear Experts,
Is it possible to get actual air flow (m3/h) of an AHU by refering to it's fan curve in a specific frequency by having actual kw of the fan?
It is a backward centrifuge fan with exact curvd in different frequency and power.
Actual power kw and actual RPM is displayed on VFD...
Thanks for your reply,
The filter air flow m3/h should be higher than or equal to AHU air flow m3/h? Because as far as I know final differential pressure of the filter is given in nominal flow of it so I should order a filter with a air flow equal or higher than AHU flow.
Am i correct?
Hi dear Experts,
I have seen a differential pressure switch across a heat recovery wheel in some AHUs.
Could you please let me know the function of the DPS and how it should be adjusted.
Regards,
Dear Experts,
Could you please let me know what parameters should I consider to order a new G4 filter for AHU.
Unfortunately there is no data on the current installed G4 filter.
Any relationship bettween AHU air flow m3/h and filter air volume?
Regards,
Thank you for the reply @MedicineEng
In our AHU the fresh damper is always 30 % and mixing damper is 70% and only in free cooling mode the fresh air damper become 100% so with this case how should i adjust the differential pressure switch across the filter G4 ?
Dear experts
I have read some manuals from different expansion tanks' manufacturer and they have mentioned the expansion tank air side pressure should be 0.3 bar higher than the static pressure of the point to which the tank is connected.
If the air pressure of the tank is the same static...
Thank you so much for the reply
To be honest there is neither data available from the designer nor any diagram.
You are completely right I need to get some
actual value then decide about the situation.
Dear @EnergyProfessional could you please let me know how a fan coil should be controlled by...
Yes the actuator is analoge type (0to 10v) and the fan coil is 4pipe type
Two picv valves are used to control cooling and heating coils
The valves are controlled from BMS system and a dedicated controller from siemens. The actuator percentage is controlled by the room temperature but the...