Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by Siyou

  1. Siyou

    CB Short Circuit Rating

    Does the momentary short circuit calculations also called the first cycle calculation???? Can you state why did sometimes its called half cycle calculation??? Does the momentary symmetrical rms current, momentary asymmetrical rms current and momentary asymmetrical peak current based in what...
  2. Siyou

    CB Short Circuit Rating

    Why it is important to compute the momentary symmetrical rms current,momentary asymmetrical rms current and momentary asymmetrical peak in the evaluation of CB short circuit ratings? Does the momentary asymmetrical peak short circuit current and the interrupting symmetrical rms short circuit...
  3. Siyou

    CB Short Circuit Rating

    Can I ask if the rated short circuit amps in nameplate is the interrupting symmetrical rms current rating? The nameplate has only the rated short circuit amp on the nameplate which is 25kA., with 3 cycles and voltage range factor of 1.0 . How can I know the momentary rating or the making current...
  4. Siyou

    CB Short Circuit Rating

    Do you have tables for the short circuit rating of CB in ANSI at IEC used in high and medium voltage?
  5. Siyou

    CB Short Circuit Rating

    Do you use safety margin in comparing the calculated fault currents to the Cb rating?what if the safety margin is 330% what does it mean?? Do you have TABLE FOR standard kaic ratings IN ANSI and IEC?? THANK YOU
  6. Siyou

    CB Short Circuit Rating

    Hello everyone! How to evaluate CB short circuit rating based on the calculated short circuit current? How many percent must be the calculated fault current compared to CB short circuit rating? Do you have standard CB short circuit ratings table for ANSI and IEC CB? Thanks everyone
  7. Siyou

    ETAP

    How did ETAP solve for the device capability of the momentary and interrupting summary report? Thank You
  8. Siyou

    Typical X/R ratio for transformer and induction motor

    How did ETAP solve for the device capability of the momentary and interrupting summary report? Thank You
  9. Siyou

    ETAP

    Hello everyone! How did ETAP solve the base value on its short circuit report manager? How can I also solve for the per unit impedance of my transformer if the rating of the transformer is 67kV/13.8kV... my base voltage that I used is 69kV/13.8kV since that is connected in a 69kV/13.8kV...
  10. Siyou

    Typical X/R ratio for transformer and induction motor

    @ Xnuke so what will I use? low, medium or high? The low, medium and high graph has its own X/R values. I dont have the data of the X/R ratio of transformer and induction motors for my short circuit calculation, thats why I will be using the typical values from IEEE standards, but sadly the low...
  11. Siyou

    Typical X/R ratio for transformer and induction motor

    Hello everyone! Can I ask what is the meaning of low, medium, and high on the graph of the typical X/R ratio of transformer and induction motor in IEEE standards? Attached here is the picture of the typical X/R ratio. Thanks...
  12. Siyou

    Time Constant of Circuit Breakers

    Will I used only the symmetrical breaking current result or the asymmetrical breaking current to compare with the nameplate breaking current? How can I evaluate the result based from the short circuit rating in the nameplate? The X/R ratio is greater than 17
  13. Siyou

    Short Circuit Calculation

    The 69kV line uses a CB which has a rating in IEC standard, while on the 13.8 kV it uses ANSI standard.. So meaning I will do twice short circuit calculations ANSI and IEC?
  14. Siyou

    Short Circuit Calculation

    Thanks Everyone. If I dont have the fault duty of the utility source, what can I used?
  15. Siyou

    Short Circuit Calculation

    Do I need to calculate the asymmetrical breaking current and dc current component and use this in the evaluation of the IEC rated CB? How about if the asymmetrical breaking current calculation is higher as well as the dc current, does it shows that the calculations exceeds the device capability...