Typical X/R ratio for transformer and induction motor

Status
Not open for further replies.
Replies continue below

Recommended for you

X/R values vary depending on construction, so the graph offers you an envelope within which they normally will fall.
 
@ Xnuke so what will I use? low, medium or high? The low, medium and high graph has its own X/R values.
I dont have the data of the X/R ratio of transformer and induction motors for my short circuit calculation, thats why I will be using the typical values from IEEE standards, but sadly the low, medium and high graph has no meaning if what does this low, medium and high are for.
 
OP said:
I dont have the data of the X/R ratio of transformer and induction motors for my short circuit calculation,
Use the impedance voltage to calculate the symmetrical short circuit current.
Use this value to match switch-gear ratings.
For mechanical forces on supports, the worst case, 100% offset, asymmetrical current will approach 2.83 times the symmetrical short circuit current. (2 x Root 2)


Bill
--------------------
"Why not the best?"
Jimmy Carter
 
How did ETAP solve for the device capability of the momentary and interrupting summary report?

Thank You
 