Hi everyone,
I am wondering for those of us who are based in Australia, could we use the calculation methodology as per HB101 and HB102 for AS3835 to evaluate the AC induction voltages for a pipeline?
The AS3835 is titled "Earth Potential Rise - Protection of telecommunications network users...
Hi all,
Where we use X90 and X110 rated XLPE cables and we "push" the cables to run at a higher ampacity with a higher conductor operating temperature, say we take 80deg in this instance.
If we run these cables in PVC conduits (typically buried in-ground), would these PVC conduits not be an...
Thanks VTer. If I calculate the value using the formula you mentioned, i.e. 400A/3 x 11kV x Sqrt(3) = 2540kVA. Surely that is too big a size?
Thanks RRaghunath. I also think the IEEE is a bit more correct - but I am not sure why there is such a big discrepancy with the Westinghouse T&D which is...
Hi all,
I am trying to size the kVA rating of the zigzag TX. The parameters are:
11kV, Ineutral = 400A, 60sec rating.
Based on Westinghouse T&D book, the rating is calculated to be 11kV/sqrt(3) x 400A x factor of 0.104 = 264.2kVA.
Based on IEEE C62.92.4:2014, the rating is calculated to be...
Happy new year 2021 to everyone.
In the CDEGS FDIST module, I want to define a terminal using underground 11kV cables. I am trying to get to the user interface where it shows the following (the screenshot below is taken from the manual) but I could not find a way how to get to this screen...
Thanks waross.
Thanks Dave.
I have now saved the higher resolution pictures, accessible via the following links. Could I please trouble you to have a look please?
Current paths - fault at generator bus
S/C currents for fault at generator bus
Current paths - fault at generator winding
S/C...
Thanks waross. Appreciated your help.
I will double check the input for the zigzag transformer as per your advice. But magnitudes of fault currents aside, could you please have a look at the fault current paths as per my markups above? I would like to know if the fault currents do indeed travel...
Thanks pped, waross, dave.
I think I finally got the idea now and to make sure that I actually understand it all, I markup the following sketches to show the current path flowing when the fault is at the generator bus and when the bus is at the internal winding. Could you please have a glance...
Thanks again Dave.
Following your recommendation, I have now added a short section of cable from the generator bus to the generator and adding a bus to it. This looks like the following:
Then I simulate a generator bus fault and observe the fault levels with 1 x generator connected, 2 x...
Thanks Dave for your comments.
Although I work in the IEC world, sadly for HV earthing of generator there are no known IEC standards or references I can draw upon. I stand corrected so if anyone has a suitable IEC references please do tell.
The current HV generator earthing design is drawn...