tofulover
Electrical
- Jun 17, 2020
- 40
Hi all,
I am trying to size the kVA rating of the zigzag TX. The parameters are:
11kV, Ineutral = 400A, 60sec rating.
Based on Westinghouse T&D book, the rating is calculated to be 11kV/sqrt(3) x 400A x factor of 0.104 = 264.2kVA.
Based on IEEE C62.92.4:2014, the rating is calculated to be 11kV/sqrt(3) x 400A / sqrt(3) x 7% = 102.7kVA.
Not sure if I am calculating this right and why there is such a big discrepancy? If this is incorrect please advise the right method?
Thanks in advance.