You need a zigzag transformer that will provide you a neutral that you will connect through a grounding resistor. The size of this resistor will determinate the size of the zz transformer.
As the project manager couldn't find anything wrong with the motor or the distribution system, he decided to replace the VFD. His company has several across the country, so they'll try another one.
Adding more details here:
Motor has been tested and is in good shape. The drive however is burning parts on the control board: MOV, capacitors.... The newer drive installed 2 weeks ago is already showing signs of burning. Application is using 47 Hz, its not at full speed. I've been asked to...
Field testing of some Eaton closed transition ATS's gave paralleling delays in 80-90 msec time window. An alarm is set at 100 msec that stops the process, if need be.
DSP MKII is a ground fault relay. It comes with a grounding resistor. It's the vintage model of the I-gard.
If you have feeder modules, it will tell you which phase is grounded and on which feeder. It leaves you live with one occurring ground fault (Alarm). If you get a second ground fault on a...
This SDP module should be installed right into the switchgear. 8 feet distance is too large and protection is lost. Our manufacturer states a max cable length of 14 in! And we use 30 A breakers. Not much current flows into this, only high voltage transient surges.