Recent content by zimmerDN

  1. zimmerDN

    Relay Contact Life

    itsmoked, Thanks for the reply. Can you help me understand what you mean? Do you believe the curves (attached) that are published only suggest the mechanical life? Therefore any arcing will further reduce the life of the contact beyond what's stated on those curves? Why do they publish...
  2. zimmerDN

    Relay Contact Life

    Hi I want to estimate the relay contact life that is switch some 120VAC solenoids. The manufacturer provides a graph listing expected operations VS switching current. That's quite easy to follow if you have one solenoid being switched by the contact. Question #1 But how do you determine...
  3. zimmerDN

    Installing TEW & SEW Wires in Conduit

    In order to be in compliance with the CSA or Ontario Electrical Safety Authority (OESC) code, Can TEW machine wires or SEW appliance wires be installed in a conduit as interconnecting wires to provide 120VAC power from a transmitter to a remote sensor? I'm looking for 90+ Deg C rated wire to...
  4. zimmerDN

    Slow LCD Display in Cold Weather

    Hi I want to some feedback from others on this site. I have a touchscreen rated to -20C that's mounted outdoors but the response is often very slow and laggy during cold weather months. It often dips down to -10C around here. A slow touchscreen is a major annoyance for the users. I am...
  5. zimmerDN

    Transformer with the same primary & secondary voltage

    One disadvantage I can think of is if the load at the end of this circuit suddenly drops and voltage drop is reduced then the transformer might be suddenly be over compensating creating a power surge. Are there auto tap changers in a transformer? Are they reliable? What about a voltage...
  6. zimmerDN

    Transformer with the same primary & secondary voltage

    Is it good (and common) practice to use isolation transformer to boost the voltage? What is the limitation on boosting the voltage and are there any drawbacks to using isolation transformer?
  7. zimmerDN

    Transformer with the same primary & secondary voltage

    Does this type of transformer exist? Primary and Secondary voltages are both the same, 600V, but it's Delta to Wye connected, 3-phase, ~400KVA. The reason for asking is, I want to take advantage of the taps in a transformer to give a small boost to voltage that is too low. Can this be...
  8. zimmerDN

    AB 1756 Controller Watchdog

    I want to send set an alarm bit when the controller faults on minor or major watchdog error. I was thinking about using the GSV (Get system value) function to read the controller Fault Log. Should this logic be placed in it's own separate task and set as a periodic task type. If the main...
  9. zimmerDN

    Oversize Primary Fuse on Transformer

    What is the reason that the code allows 125% primary o/c protection on a transformer and is it common/best practice to do so without secondary o/c protection?
  10. zimmerDN

    Oversize Primary Fuse on Transformer

    The CEC code allows the use of overcurrent protection device rated at 125% of the rating of a dry type transformer with primary voltage below 750V, overcurrent protection on the secondary side is not required. Are the transformers built to withstand the load at 125% for long periods of time...
  11. zimmerDN

    Resistance / Voltage Drop Across a Contactor

    What is an acceptable level of voltage drop across the line and load side of a motor contactor? Is there an IEEE standard or manufacturer recommendation on this?
  12. zimmerDN

    3-Phase Transformer, 1-Phase Loads

    DPC, If it can carry 30KVA, would that be 30,000/120 = 250A on L1-N, L2-N, L3-N if they are all balanced 1-phase loads? To the transformer these are the equivalent of 250A / (120/208v) / 1.73 = 83A across L1-L2, L2-L3, L1-3?
  13. zimmerDN

    3-Phase Transformer, 1-Phase Loads

    How many amps of 120V single phase loads can a 3-phase 30KVA, 600V - 120/208V transformer delivery on L1, L2 & L3? What about 208V single phase loads? I understand that you can have 30,000/208/1.73 = 83A of 3-phase 208V balanced loads but I want to understand the single phase 120/208 scenario.
  14. zimmerDN

    Power Grounding

    So in a ground fault sitution, you rely the electrical path created by the bonding wires which the fault current will travel on in order to return to the source (ie transformer). This low resistance short circuit (even lower in resistance than the path to earth ground) will cause enough current...
  15. zimmerDN

    Power Grounding

    Why won't the overcurrent protection work? Wouldn't the magnitude of fault current be the same in either cases (with or without the bonding between the two earth grounds, see picture above) and the o/c will trip because of excessive current. Why would the magnitude of the fault current be...