The CEC code allows the use of overcurrent protection device rated at 125% of the rating of a dry type transformer with primary voltage below 750V, overcurrent protection on the secondary side is not required.

Are the transformers built to withstand the load at 125% for long periods of time? Is the 125% primary o/c rating to allow for in-rush?
 
Replies continue below

Recommended for you

I would expect the 125% is so the transformer can operate at full load without blowing a fuse but inrush could be about ~10 times the full load of the tranformer so I wouldn't consider it is setup to "allow for inrush."
 
What is the reason that the code allows 125% primary o/c protection on a transformer and is it common/best practice to do so without secondary o/c protection?
 
Is't there any thermal protection to take care of overload? Fuses are usually not at all there for overload protection.

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
In Canada and probably the US it's a code issue. Most fused switches and breakers are approved for continuous operation at 80% of the rating. In order for a transformer to deliver full rated current to a continuous load, the fuses or breaker must be 125% oversized.
Rule 8-104 (5),(a)
Most continuous loads are required to be supplied with conductors and overcurrent devices rated or set at 125% of the load current as a code requirement.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 