Bolts and T-Stubs and Prying, Oh My! 2
human909
2,114
I hope the title caught you attention, and I hope you are enthused to have your thinking caps on.
So we as good engineers know that, we should use thick/(or gusseted) plates when we are designing connections with significant tension loads. A big part of this is so we can use a rigid plate approach and simplify connection design and reduce prying forces on our bolts.
But what about when we don't have a rigid connection under tension? What do we want to accept as satisfactory?
Exhibit A:
1738231879704-jpeg.4174
This is the bottom chord and walkway of a 20m truss gantry. This is a very ugly connection under tension as it is the bottom chord.
The bottom chord is HSS(125x125mm) and the verticals are 125x10Angle. 2xM24 bolts above and below the HSS chord. It is pretty clear that the 10mm plate section of the angle isn't stiff enough for the load here. (At a guess 25mm plate would be better)
This deflection is under dead weight only (which is about 80% of service load and 40% of ultimate load.) Bolts even with prying are more than satisfactory and the plate is unlikely to fail (I have yet to explicitly calc this out). How would you deal with this situation? Would you reject it? Perform significant rectification? Accept it if it calcs out?
Any thoughts appreciated.
Looks like some strap plates are needed, positioned like your tape measure.
Great idea. I was already thinking welded plates. But you description of 'strap plates' made me think of a bolted approach. Either blind bolts into the HSS or through bolts picking up plates either side.
As mentioned above. I'm passing the responsibility for the design of this to those originally responsible. But that doesn't prevent me from nudging them in a particular direction. ;)
(Bolting strap plate will mean backing off the bolts in the original connection to transfer the load. But I don't see an issue there...)
The only potential issue I see is that it might open slightly more before the bolts engage. In these situations, minimal bolt clearance is highly beneficial. There's no need for the standard 2mm oversized holes. You can clamp the plates on, drill the holes with the mag drill, and thread the bolt straight in.
Welding works too, and avoid all the issues of bolting, except then you're welding gal steel. Not necessarily the end of the world...
Haven't read all replies. Would quote limit on Ze from commentary to avoid service load yielding. Extend principle here. Doesn't meet code intent. Recommend fixing but owner decision if only serviceability problem.
I'm a semi-regular user of IDEA Statica. I don't think this would be overly difficult to model. I don't think an FEA model would tell you anything you don't already know about this connection.
This connection detail sucks. Pure speculation here, but it seems to me this is a "pre-designed" modular component from the manufacturer. In my experience, these items have potential to be poorly designed, or not designed at all. The detail is great from a fabrication perspective as they're using the vertical member as connection material for the chord. But now if the end plate thickness doesn't work you either need to add another component to the connection or increase the thickness of the entire vertical member. Same idea with the channel splice at the bottom.
The 6mm channel web has no business acting as an end plate transferring any considerable amount of load. Especially with the bolts that far from the chord. It shouldn't take FEA or even a calculator to determine that this isn't a good idea. See above comment about poor design work, or complete lack of design.
I think Tomfh is right with the strap plates. If this thing doesn't need to move anytime soon I'd be looking at welded reinforcing. I'd also discount any strength provided by the existing detail - those are erection bolts now.
The only reason to look at FEA would be to prove to those who will incorrectly suggest this is a fit up problem before they agree to fix the problem. It would also be interesting to see the effect on the webs if you have a lot of stretched connections along the length of the chords. Beyond that, the problem is obvious as suggested.
Thanks all. Some great and helpful replies here. We all seem to be on the same page.
Agreed. For interest I did a quick FEA of the model as I have the 3D available. No consideration of the welds just a fully homogenous piece. And it revealed nothing surprising. A struggling PFC, that is saved somewhat by the stiffness of the vertical angles.
This was an engineered item. However it did take a previous poor design (that has been in place for a decade or so) and designed a new truss with loads on it with poorer detailing. The result is what we see.
Agree.
An update if anybody is interested.
"Strap plates" along the lines of what @Tomfh had suggested was my suggested approach to problem. The responsible engineer was not happy with this solution as it wouldn't tension up the join and close up the gap. I don't see this as an issue, I'd prefer a clear strong and reliable load path. Sure, to load up the strap plates, it would be necessary to back off the "erection" bolts and you end up with a permanent gap. But the outcome is satisfactory, the increased gap would somewhat increase deflection but that isn't a concern here.
Instead the responsible engineer is wanting to keep the existing bolts as the load path and just stiffen the web of the channel with a stiffened plate. His solution is IMO barely adequate and a nightmare to install. When quizzed on the feasibility of installation (as existing bolts would need to be removed) he suggested a crane to take the load during the installation. This would be a delicate AND expensive process that IMO would require close engineering oversight rather than relying the contractor onsite.
I'm attempting to implement a compromise and install permanent members to engage the chords to take the load AND tighten the gap and then the solution from the responsible engineer can be implemented. This will result in a belt&braces approach. But at the moment I just want to make sure I am happy as well as the responsible engineer.
It has become complicated because the responsible engineer's solution isn't to my satisfaction. My role here is more holistic as I'm salaried by the design&build contractor so I both need to ensure structural soundness and a practical, suitable and ideally economical solution.
(And in case anybody is wondering, all my dealings with this engineer have been entirely friendly and civil. Just because we disagree about a solution doesn't mean we shouldn't be civil. :))
Another update in case anybody is interested.
It has taken an extraordinary amount of time to design, detail and get two parties to approved a suitable rectifications approach on this issue. All unfortunately at the expense of the D&C contractor. IMO it just shows how expensive a minor mistake can be. In this case I doubt there would ever be failure if left unaddressed. But there is already yielding occurring so playing that game isn't one I want to bet my reputation on.
The solution that is going to be implemented is flange stiffening as desired by the EOR. AND strap plates as desire by myself as it is a belt and braces approace and once you have implemented the former, then implementing the latter is trivial. Implementing the flange stiffening requires removal of bolts under load so a method of load removal is required, in this case it is aimed to be achieved through tensioned side plates. The EOR suggested getting a crane in as a 'simple solution' but I don't believe taking partial load is ever a simple solution. Nor is it cheap due to the loads involved and the access for the crane is difficult.
Anyway. This is more a rant than much else. A minor mistake by another engineer will result in ~$20k extra costs after all is said and done. Small costs in the scheme of some projects, but it is just a reminder to do things right the FIRST time.
Are you able to post a sketch of what is proposed as the solution? I'm curious how this all comes together but visualizing it is throwing my head in a spin.
