Pipeline Drainage - Simplified Approach
Jack.C
Industrial
Feb 17, 2023
18
Kindly asking for your help on belows query.
Let's assume a 10km long DN1000 pipeline with 3 drains at the low points. The initial head is H1 (orange line).
After a time step dt a certain amount of water has left the system (I'm using the Toricelli approach) through the 3 drains.
How would you calculate the head drop / new head H2 in the system? I would like to avoid a complex numerical equation to calculate the drop but rather go with a simplified approach.
Our simplified approach is shown in the red box in the below figure.
Please note that we are aware that the head line will behave different for the individual sags once it is equal to the height of the profile. So at one point Q1 and Q2 will drain the sag 1 whereas Q3 will drain sag 2 and that there will be different heads in these section. This will be considered.
Your inputs would be highly appreciated.
Thanks and regards!
This assumption is not reasonable.
If the valves at both ends are open, the max flow will be at Q3 since the deepest one. The size of the PL 1000 mm and length 10000 m.
The simplest approach would be calculate the amount of discharge for each drain , find the total discharge then corresponding head drop.
Hi Hturkak. The valves at both ends are closed. We are aware that Q3 is highest. But the question here is how to calculate the head drop. Regards, Jack.
If the valves at both ends are tightly closed and if there are no air valves at high points, this will be completely another story.
The pressure will rapidly drop with a small amount of discharge and vacuum will develop at high locations and if the heights of discharge points more than suction head, water will start to evaporate .The variables are not only diameter , heights but also temperature , altitude ...
We are aware that there must be air vents installed to avoid vacuum in the pipeline during drainge. The question is related to define a simplified approach to evaluate the head drop over time. Let's leave the temperature, altitude effects etc. away as this would not lead to a simplified approach.
You can't simplify something which you have shown to be quite complex.
If you place the air vents at the high point and open or have one on the valve at the left hand side would be a start, but that hump before the valve on the right messes things up quite a lot.
Actually what am I saying. The head H1 in a closed liquid system (valves closed both ends) will drop pretty much instantly to the high point to the left of the valve on the right. The amount of liquid to drop a closed in liquid head will be <0.5% of the total volume That is a relatively simple calculation about bulk modulus and expansion of the pipe. After that you really need to allow air into the system.
If the low point at pt Q3 is less than 10m below the high point then all flow will just stop until air is let into the system. If its more than that then you will start to pull a vacuum at the high point and probably also just next to the valve on the LHS.
Could you provide the elevations and horizontal km locations of the high and low points in the piping. I might have a solution.
Hi LittleInch
Thanks!
Let's assume that there is sufficient air intake capacity provided. All we are trying to understand is how the HGL will drop over time when the drains are open. At some point of course the HGL will be at the level of that hump on the right. So there will be water remaining in this section between hump and right shut-off valve.
Then at some point the HGL will reach the intermediate hump. Then Q3 will only contribute to the HGL decrease between "small" and "big" hump. Q1 and Q2 will drain the section between left shut-off valve and intermeidate hump.
Kind regards
We could just assume something. I also randomly generated the profile and the amount and locations of the three drains.
Let's assume:
Lowpoint / Q1 at KP 02+500 / Elevation = 22 masl
Lowpoint / Q2 at KP 05+000 / Elevation = 20 masl
Lowpoint / Q3 at KP 07+500 / Elevation = 10 masl
Highpoint 'small' at KP 06+000 / Elevation = 25 masl
Highpoint 'big' at KP 08+500 / Elevation = 30 masl
My point is that "at some point" will be very rapid as the volume of a liquid which relates to head / pressure above ground level high point for a totally liquid filled pipeline is very small, probably less than 0.5% of the total volume. It's called line packing and whilst many people would say a liquid is incompressible, the reality for a 10km line is that it is "virtually" incompressible, i.e. you can shut off one end and continue pumping at the other end and the pressure / height increase, but the volume required to do that is very small. Does that make sense?
Thanks for the response. Unfortunately, not. I don't understand why we have to think that complex - or is there no way to simplify it? There is no pump. There is an isolated pipeline filled with water that is being drained with 3 drains (length of pipeline is not relevant, amound of drains is not relevant. Above figures shows some random example). Let's assume it is under pressure initially. Doesn't have to but let's assume it.
Then from that the 3 drains are being opened. Here we can assume that the drain valve throttles to 5 m/s so we don't have very high flow rates in the beginning...
The drains are open, the water leaves the pipeline and the volume inside the pipeline decreases.
The issue I have is that your OP and the replies make it seem like there is a large volume of water to be drained before the head of the liquid reaches the height of the highest point. There isn't.
This is actually quite a complex issue as there are three drain points at different heights and locations along the pipeline and three different vent points, but initially only one, then two then three start letting in air. Also your driving force (head of liquid) is constantly changing so the flow out, assuming its a fixed orifice / drain valve size will be constantly changing so this is really a job for a transient analysis or you need to break it own into at least 10 steps.
Drain downs are notorious for being difficult to get a good answer and a key question is when do you decide it's all drained? First 50% could take 10 minutes, the next 45%, 50 minutes, the next 4% 40 minutes, but the last 1%?? hours / days before it stops dribbling out.
OK thanks for the information. Just curios though, why are you trying to figure this out? Is there a real life issue with the pipeline operation or maintenance during a shutdown that you need to know how the HGL varies over time?
With this set up it's impossible to get a continuous flow out of these drains. You need to install vacuum breakers at high points and then you will have subsystems to work with.
BTW, I'm puzzled with the size of the drains DN50 vs the total volume to be drained, estimated to be over 10 000 m3.
Why do you need the Height of liquid versus time? Normally people will check for the time to drain the volume.
Somewhere it looks to me like the drainage of a tank vs time, applying Bernoulli.
Good luck,
Pierre
I have done an approximate calculation making some assumptions.
The initial hydraulic grade line is at the top of the highest point. If you stop flow in the system and open vents to depressurize with end valves closed then the pressure should almost immediately go to atmospheric. There is some stretching of the pipe under pressure which will keep the pipe pressurized until unstretched and pressure goes to zero but the time is relatively small and a complex calculation so I would just ignore it.
Flow out at a given time is based on the sum of the 3 drains flow as indicated in the calculations. The calculation is done in steps such that you calculate the flow at the beginning of the step, multiply it by the time step to get the total volume out, then calculate change in height. Repeat this process for a line segment until the sum of change in height of equals the total height of the segment.
I did the first two line segments in the calculations which I broke up into points A, B and C in the diagram. The first segment just drains the right end. The second segment drains both the right and left end. This is why I separated those two segments. Note that during the first segment draining the vents at the left end above point B to the left of the intermediate hump needs to be closed or flow will be out those vents.
Once you get to the intermediate hump then the flow will be split to drains 1 and 2 on the left side of the intermediate hump and drain 3 on the right of the intermediate hump. At this point you can set up the flow and change in height equations as I did to suit this configuration and to find change in height versus time.
I assume for the 2" drain lines the total equivalent length was 10 feet with friction factor 0.019 at turbulent flow. If you have more length of 2" drains then you need to adjust the calculations.
The equation you show on your pipe diagram sheet is basically correct for a pipeline with a constant slope from one end to the other where Q dT is the same equation I have for Q in my calculations (base on 3 - 2" drain lines) times the chosen time interval.
  • Pipeline Draining Question3.pdf
