Using Bond Breaker vs Sleeve for Anchor Bolts to address Ductility
oengineer
730
In PIP STE05121 Application of ASCE Anchorage Design for Petrochemical Facilities it says the following:
“In the case of larger diameter anchors, the only relevant applications for using a sleeve are to provide stretch length to meet the requirements for the anchor to be a ductile steel element or where the anchor will be tensioned.
Would it be structurally acceptable to wrap the anchor bolt with Bond Breaker Tape instead of using a sleeve to meet the requirements for the anchor to be a ductile steel element or where the anchor will be tensioned?
Comments/suggestions are appreciated.
Yes ... you can eliminate the sleeve but the use of sleeve is necessary for precise alignment of anchors when required during installation of the equipment .
Yes ... you can eliminate the sleeve but the use of sleeve is necessary for precise alignment of anchors when required during installation equipment .
If a template is being used to place the anchor bolts for the vertical vessel, would that take care of the alignment of anchors required during installation equipment?
Template will help for the positioning of the anchors at the top of the foundation but does not ensure verticality precisely. If you are sure for the quality of workmanship, IMO yes OK .. delete the sleeve and wrap with electric tape for bond breaking .Moreover ,in this case the anchors can resist to shear.
