The CBC (mostly IBC) allowable soil pressures may be increased by 1/3 for seismic loads that use the alternative load combinations, and geotech engineers typically allow a similar increase in their reports.
ASCE 7 12.13.4 allows a 25% reduction to overturning loads, and CBC does not allow this when using alternative basic load combinations.
Thus ASD would be 0.6D + 0.75(0.7E) and alternative would be 0.9D + E/1.4 with 1/3 increase in allowable soil pressure. Would you assume that the 25% reduction in overturning loads should not be used with the 1/3 increase from virtually every geotech report? Or is it acceptable to use the increased soil capacity with ASD load combinations and the 25% reduction in overturning forces? Maybe a question for geotech engineers but maybe more of a code-intent question.
ASCE 7 12.13.4 allows a 25% reduction to overturning loads, and CBC does not allow this when using alternative basic load combinations.
Thus ASD would be 0.6D + 0.75(0.7E) and alternative would be 0.9D + E/1.4 with 1/3 increase in allowable soil pressure. Would you assume that the 25% reduction in overturning loads should not be used with the 1/3 increase from virtually every geotech report? Or is it acceptable to use the increased soil capacity with ASD load combinations and the 25% reduction in overturning forces? Maybe a question for geotech engineers but maybe more of a code-intent question.