rockman7892
Electrical
- Apr 7, 2008
- 1,156
I'm specifying wye-wye PT's on a 34.5kV system that is a Delta system but grounded through a zig-zag transformer with NGR. Can these PT's be standard 20125/35000 GRD Y single bushing PT's or do they have to be a 2-bushing PT for potential elevated L-G voltage during a ground fault?
I know typically on ungrounded or impedance grounded systems the PT's require 2-Bushing PT's rated for full L-L voltage that would be present during a ground fault. In this case it would be a 20125/35000 Y rated PT.
Also I was looking at a PT that had a rating nomenclature of 34500/34500 GRD Y. What does this rating indicate? Why is the L-L voltage repeated twice on here?
I know typically on ungrounded or impedance grounded systems the PT's require 2-Bushing PT's rated for full L-L voltage that would be present during a ground fault. In this case it would be a 20125/35000 Y rated PT.
Also I was looking at a PT that had a rating nomenclature of 34500/34500 GRD Y. What does this rating indicate? Why is the L-L voltage repeated twice on here?