The effect will dpeend on your system curve and pump curves, but for a 1 + 1 system for centrifugal pumps with a DOL starter, you're probably looking at 3-4 seconds for full wind up of the spare pump and then no more than 5 to 10 secods before you want to turn your first pump off without seeing any major increase in flow. You won't increase pressure that much, but might bump the flow up briefly, unless you have some sort of flow control downstream of the pumps. If you run two pumps for any lenght of time , say > 10 seconds, then you're operating as a parallel pump set up - see the other posts on this page which will tell you all you need to know about that. If you run two pumps for a while in parallel and then turn one off, the flow through the remaining pump can stop briefly until the downstream pressure and flow decays back to normal. This might be Ok, but if you have any no flow switches or alarms, they may need to be disabled for this period or given a longer time before shutting your pumps down.
PD pumps on the other hand will more or less instantly double the volumetric flow rate and it is unlikely that your downstream system will be able to cope with that without a large increase in pressure, possibly either causing the systme to shut down or lift the bypass or pressure relief systems if run for more than few seconds together. Rapid (5 seconds) turn off of the main pump is recomended unless yur system can cope with two pumps running. Only you can tell.
Transient analysis is the only way to really see what would happen.