Dear Experts,
I would like some input on an HVAC/Chiller problem (oppurtunity).
Given:
10000 ft^3 semi mobile building. (probably will never move)
12-15 volume changes/hour (2000-2500 CFM)
Desired air supply 68 DB 50% RH
100% Outside Air.
Outside air conditions: worst case 90 DB 90 RH.
THe trick is that this customer will be making many of these mobile facilites and they want the same one no matter where they go in the US. I am trying to convince them that this is not practical. That issue aside, my questions are:
Since this is 100% outside air, I have been calculating the coil load by CFM*dH(plus the conversions required). Do I also have to account for the sensible and latent loads in the room even though they will not "touch" the cooling coil?
When I am mostly only needing dehumidification, what would be the best soure for reheat? I have condenser exhaust from an adjacent process chiller and the superheated compressor discharge. Or do I need to look at hot water or duct heaters?
Right now I don't have any controls selected, so I can select and program those to fit my application.
Yes, we have to have 100% ventilation due to air quality issues.
Thanks in advance for any input.
Clyde
I would like some input on an HVAC/Chiller problem (oppurtunity).
Given:
10000 ft^3 semi mobile building. (probably will never move)
12-15 volume changes/hour (2000-2500 CFM)
Desired air supply 68 DB 50% RH
100% Outside Air.
Outside air conditions: worst case 90 DB 90 RH.
THe trick is that this customer will be making many of these mobile facilites and they want the same one no matter where they go in the US. I am trying to convince them that this is not practical. That issue aside, my questions are:
Since this is 100% outside air, I have been calculating the coil load by CFM*dH(plus the conversions required). Do I also have to account for the sensible and latent loads in the room even though they will not "touch" the cooling coil?
When I am mostly only needing dehumidification, what would be the best soure for reheat? I have condenser exhaust from an adjacent process chiller and the superheated compressor discharge. Or do I need to look at hot water or duct heaters?
Right now I don't have any controls selected, so I can select and program those to fit my application.
Yes, we have to have 100% ventilation due to air quality issues.
Thanks in advance for any input.
Clyde