neher
Electrical
- Apr 18, 2015
- 11
I have a feeder that draws 900A continuously
I specified 1000A 100% rated LSIG breaker.
The submital i am reviewing calls for a 80% rated 1200AF with a 1000AT LSIG trip unit.
Never really thought about it before but is the breaker rating (100% rated VS 80% rated) for the frame or the trip?
When an elephant is in trouble even a frog will kick him.
I specified 1000A 100% rated LSIG breaker.
The submital i am reviewing calls for a 80% rated 1200AF with a 1000AT LSIG trip unit.
Never really thought about it before but is the breaker rating (100% rated VS 80% rated) for the frame or the trip?
When an elephant is in trouble even a frog will kick him.