I am upgrading protection on two 2.5MW diesel engine gen sets with groundng reactors. My spec required Schweitzer SEL-300G relays, and also called out ANSI 64G - 100% Stator Ground protection.
We recently met with the protection designer, and he said that a 64G was not appropriate for these generators. I read through the 300G manual, and the manual says that 64G is recommended for high impedance systems.
Who do I believe? Schweitzer's manual, or the protection engineer who by his own admission, is not overly familiar with SEL gear.
Thanks!
We recently met with the protection designer, and he said that a 64G was not appropriate for these generators. I read through the 300G manual, and the manual says that 64G is recommended for high impedance systems.
Who do I believe? Schweitzer's manual, or the protection engineer who by his own admission, is not overly familiar with SEL gear.
Thanks!