Good day,
I have a question about an IR Test (insulation resistance) on the rotor of a 1000KVA Leroy Somer LSA 50.1 alternator. I use the Megger MIT1525 for the IR test and I'm doing a rotor to earth insulation test.
As I know from the past when performing resistance tests on other alternators & field windings , the resistance to earth should be very high (M/Ohm) or even infinity (if brand new) between any winding and earth. In the case of my Megger MIT1525, when conducting a test such as this, a rising test voltage is introduced across the tested points for a 60 second period (0VAC to 1000VAC), and at the end of the test period it will indicate to what voltage the winding can perform, breakdown resistance, and what the general resistance is between the windings and earth.
In my case, when conducting the IR test on the suspect rotor's disconnected leads and the shaft (earth), I get a warning beep and an indication on the meter display of a fault after barely initiating the 60 second test, maybe 5 seconds in, as soon as the test voltage reaches around 15VAC, that does not rise again until the conclusion of the test, and the final insulation resistance is very low and does not even register on the meter display (minimum reading is 100 Kilo Ohm)
So, my question is: Is the rotor shorting to earth and do I need to have the alternator refurbished/replaced?
At the moment I'm second guessing myself and don't want to make an incorrect judgement call.
I have a question about an IR Test (insulation resistance) on the rotor of a 1000KVA Leroy Somer LSA 50.1 alternator. I use the Megger MIT1525 for the IR test and I'm doing a rotor to earth insulation test.
As I know from the past when performing resistance tests on other alternators & field windings , the resistance to earth should be very high (M/Ohm) or even infinity (if brand new) between any winding and earth. In the case of my Megger MIT1525, when conducting a test such as this, a rising test voltage is introduced across the tested points for a 60 second period (0VAC to 1000VAC), and at the end of the test period it will indicate to what voltage the winding can perform, breakdown resistance, and what the general resistance is between the windings and earth.
In my case, when conducting the IR test on the suspect rotor's disconnected leads and the shaft (earth), I get a warning beep and an indication on the meter display of a fault after barely initiating the 60 second test, maybe 5 seconds in, as soon as the test voltage reaches around 15VAC, that does not rise again until the conclusion of the test, and the final insulation resistance is very low and does not even register on the meter display (minimum reading is 100 Kilo Ohm)
So, my question is: Is the rotor shorting to earth and do I need to have the alternator refurbished/replaced?
At the moment I'm second guessing myself and don't want to make an incorrect judgement call.