On a HRG system during a single phase to ground fault, transient over voltages are created. But not as
bad as on a 5kV or 15kV system. Comparatively the transient voltages created on a 600V system
would be little higher than on a 480V HRG system. Therefore, to protect the cable from those possible
transient over voltages, it is better if we can use a 1000V insulated cable on 600V HRG system and a 600V
insulated cables on a 480V HRG system.