Hi all,
we have 6 gas engines (0.4kv,1950kw each) connected to 11kv bus throw (0.4kv/11kv 3MVA transformers). this power station feeds residential loads in the countryside (air conditioners, water pumps, lighting, and workshops) throw 20km, 175mm2 OHL .
I noticed the following during the summer period when the station breaker is closed, the loads start to rise gradually within an hour until they reach about 380 amperes in the station breaker, then a sudden jump in the current occurs, as a result of this breaker trip, especially at peak times (at noon). And when we switch on this barker again it trip within 1 hour. But during the night or dawn period, this problem does not occur and the loads are about 320 amps in this braker.
If we observe this problem from the load side at the end of the line at the branching distributing lines, we notice that the voltage is initially about 10.6 kv when the distribution lines are disconnected, then when all the lines are connected and the load begins to rise , we notice that the voltage drops gradually from 10.6 to 8 kv within an hour and then a jump occurs in the current and a severe voltage breakdown then the main station circuit breaker trip.
The peak load is about 7MW
please see the attached SLD
we have 6 gas engines (0.4kv,1950kw each) connected to 11kv bus throw (0.4kv/11kv 3MVA transformers). this power station feeds residential loads in the countryside (air conditioners, water pumps, lighting, and workshops) throw 20km, 175mm2 OHL .
I noticed the following during the summer period when the station breaker is closed, the loads start to rise gradually within an hour until they reach about 380 amperes in the station breaker, then a sudden jump in the current occurs, as a result of this breaker trip, especially at peak times (at noon). And when we switch on this barker again it trip within 1 hour. But during the night or dawn period, this problem does not occur and the loads are about 320 amps in this braker.
If we observe this problem from the load side at the end of the line at the branching distributing lines, we notice that the voltage is initially about 10.6 kv when the distribution lines are disconnected, then when all the lines are connected and the load begins to rise , we notice that the voltage drops gradually from 10.6 to 8 kv within an hour and then a jump occurs in the current and a severe voltage breakdown then the main station circuit breaker trip.
The peak load is about 7MW
please see the attached SLD