Hello all,
I have a 1500kVA 12.47kV to 480V 3 phase transformer being installed and I was tasked with verifying the primary feeder sizing. I found another post that very closely described the situation I am facing but I have some additional questions. The transformer is being fed by a fused switch with a 100E fuse. The conductors will run in conduit underground for +10 feet and then hop in a cable tray where they will run to the primary of the transformer.
I noticed from 13.2kV Feeder Sizing that the primary conductor should be sized for the load of the transformer and future load growth. I'm good with this, but when it comes to sizing the conductors I am unsure of what I have found in the codebook (yet again).
The load of the transformer would be 1500kVA/(12470*1.732) = 69.45A. Since the highest power rating of the transformer nameplate is 1932kVA I'm thinking of using it to size the primary conductors. This comes out to be 89.45A.
I would like to use a 3/C armored cable - so, per 310.60(C)(79) - One Circuit - Detail 1 - I should be able to use MV-105 #6.
Is this correct (assuming the cable thermal damage curve coordinates nicely with the fuse curve)?
Thanks,
-jstpie5
I have a 1500kVA 12.47kV to 480V 3 phase transformer being installed and I was tasked with verifying the primary feeder sizing. I found another post that very closely described the situation I am facing but I have some additional questions. The transformer is being fed by a fused switch with a 100E fuse. The conductors will run in conduit underground for +10 feet and then hop in a cable tray where they will run to the primary of the transformer.
I noticed from 13.2kV Feeder Sizing that the primary conductor should be sized for the load of the transformer and future load growth. I'm good with this, but when it comes to sizing the conductors I am unsure of what I have found in the codebook (yet again).
The load of the transformer would be 1500kVA/(12470*1.732) = 69.45A. Since the highest power rating of the transformer nameplate is 1932kVA I'm thinking of using it to size the primary conductors. This comes out to be 89.45A.
I would like to use a 3/C armored cable - so, per 310.60(C)(79) - One Circuit - Detail 1 - I should be able to use MV-105 #6.
Is this correct (assuming the cable thermal damage curve coordinates nicely with the fuse curve)?
Thanks,
-jstpie5