Hello,
I have a 120/208 Vac panel that is fully populated and due to the nature of this panel installation there is not a need to provide additional expansion. The load is a mix of 120 and 208 lighting loads and receptacle loads (no motors etc.)
The total load on the panel is 26,688VA.
My question is: what is the minimum size main breaker that I can use to protect the panel.
I think it should be (26688VA/(208*1.73))*1.25= 92amps. So I should use a 100amp breaker.
Is this correct??