Eldon1955
Electrical
- Sep 13, 2006
- 4
I have a perplexing dilemma.I have a control system,120 volt,about 24 conductors in a single conduit.This system is fed with a 120 volt UPS system.The conduit run is about 40 feet.Conductor size is #14 awg.In this conduit are a #12 bond,four neutrals and 19 conductors some energized and some not at any given time.Their function at this time is virtually no load.Their purpose is to run indicating LEDs and two momentary contact n.o. contacts as well as three s.p.s.t. toggle switches.The conduit run is between an indicating panel with the aforementioned devices and a control panel with 120 volt control relays and two small contactors .This system is fed by a single circuit with a UPS system though I have the same problem when I bypass the UPS. The problem is I read weird small voltages at points where I should be reading zero voltage.The voltages vary from 20-40 volts from various points to neutral.Readings were taken with a Fluke 87V meter RMS.My system is all hardwired 120 volt of a single power source so I don't believe these strays will adversely affect me but they puzzle me.I can read 40 volts to the neutral with a conductor disconnected at both ends.Any ideas where this dilemma is originating and how do I get rid of it? Thanks ERC