birddogger
Electrical
- Feb 23, 2004
- 31
Per NEC 240.4(B), a 277/480V, 800A feeder is allowed to be the industry standard of 2 sets of 3-1/2”C, (4)#500, (1)#2G even though the ampacity of the feeders are only 380A. However, it seems that I’ve seen this standard applied to 1200A and 1600A feeders as well, even though 240.4(C) requires any OC device over 800A to have conducters rated equal to or greater than the device rating.
So am I correct in assuming that the proper size for a 1200A feeder would be 4 sets of 3”C, (4)#350, (1)#3/0G? Or is there some loophole I’m not aware of that would allow three sets of #500's to be applied to this circuit as well?
So am I correct in assuming that the proper size for a 1200A feeder would be 4 sets of 3”C, (4)#350, (1)#3/0G? Or is there some loophole I’m not aware of that would allow three sets of #500's to be applied to this circuit as well?