I have a 80kVA UPS (Chloride Apodys) with 120VAC, 1 phase, 60Hz output. Its a double redundant system with isolation transformers on the output side. The measured voltage at one of the consumer end is: L-N : 115VAC, N-G: 85V, L-G = 115VAC. This is a floating neutral system. The O&M Manual for the UPS reveals that neutral link to earth is available but left for the end user to be connected.
Now the queries:
a. Is a floating neutral system required for the DCS and PLC power supply ?
b. What in these power supplies causes the neutral to float so far from the ideal 0V?
c. If any other consumer cannot tolerate the N-G voltage, would separate isolation transformers solve the problem?
What sort of problem will be faced by non-DCS and non-PLC consumers?