dtlxii
Electrical
- Apr 12, 2005
- 12
I want to use a control panel enclosure with three compartments to house the main power in one, and two independent panels that get their power from the main compartment but have their own disconnect switch. They will power VFDs but also provide 120 VAC for other controls along the machines.The main panel would be Panel 1, the others Panel 2 and Panel 3.
I also want to use only one 3-phase, 480 to 208 transformer to provide the 120VAC to the two independent panels (Panel 2, Panel 3) This transformer would be connected to Panel 1.
When Panel 2 is switched on, Panel 2's 24VAC transformer will energize the coil in a 3-pole contactor (housed in Panel 1)) and power would be transferred to feed the three 120VAC lines for Panel 2 only. Panel 3 would have its own dedicated contactor, also in the Panel 1, that would energize only when panel 3 is on and provide three lines.
My question is: The secondary of the 480/208 transformer has one neutral. How do I handle this?. I think that if the neutral is shared by panels 2 and 3, even if one panel is off, the neutral will still be carrying current. Should I use a 4-pole contactor and run one neutral wire to each of the contactors? Is it better to use one 480/208 transformer for each panel? Please see attached drawing.
Thank you.
I also want to use only one 3-phase, 480 to 208 transformer to provide the 120VAC to the two independent panels (Panel 2, Panel 3) This transformer would be connected to Panel 1.
When Panel 2 is switched on, Panel 2's 24VAC transformer will energize the coil in a 3-pole contactor (housed in Panel 1)) and power would be transferred to feed the three 120VAC lines for Panel 2 only. Panel 3 would have its own dedicated contactor, also in the Panel 1, that would energize only when panel 3 is on and provide three lines.
My question is: The secondary of the 480/208 transformer has one neutral. How do I handle this?. I think that if the neutral is shared by panels 2 and 3, even if one panel is off, the neutral will still be carrying current. Should I use a 4-pole contactor and run one neutral wire to each of the contactors? Is it better to use one 480/208 transformer for each panel? Please see attached drawing.
Thank you.