A GE Turbo-Generator 25 MW, 13,800 Volts, 60 HZ, 3600 rpm, was running satisfactory and under normal condition. We stopped it for scheduled two year routine insulation test.
Phases A and B passed satisfactory Insulation Resistance (IR) at 10 kVDC for one minute, with 5800 and 6000 Megohms. The PI was 3.51 and 3.55. A controlled step voltage up to 28 kV, with 2kV/min steps followed the same results as compared with the test taken two years ago. (Around 0.5 microamperes with 10 KV and 12.5 microamperes at 28 kV).
On April 15, 2004, for phase C, the minimum Insulation Resistance (IR) tested was 5200 Megohms after 1 minute (phase C) and the Polarization Index (PI) 3.13
Controlled Over voltage Test (step Voltage Test) was done to the stator winding and phase C showed; IR = 1300 Megohms at 1 minute and PI= 2.08. The leakage current showed deviation as compared to the curve of previous test results, the test was stopped at 22 kV and 79 microamperes leakage. On April 19 the stepped voltage test on phase C was repeated and stopped at 16 kV with 31.2 microamperes leakage, to prevent imminent insulation breakdown.
Questions:
Will this generator stay operational until a scheduled outage for rewinding?
Should we stop the generator now and proceed with rewinding?
The difference of the costs involved with the decision is quite big, rewinding now being the most expensive.
Phases A and B passed satisfactory Insulation Resistance (IR) at 10 kVDC for one minute, with 5800 and 6000 Megohms. The PI was 3.51 and 3.55. A controlled step voltage up to 28 kV, with 2kV/min steps followed the same results as compared with the test taken two years ago. (Around 0.5 microamperes with 10 KV and 12.5 microamperes at 28 kV).
On April 15, 2004, for phase C, the minimum Insulation Resistance (IR) tested was 5200 Megohms after 1 minute (phase C) and the Polarization Index (PI) 3.13
Controlled Over voltage Test (step Voltage Test) was done to the stator winding and phase C showed; IR = 1300 Megohms at 1 minute and PI= 2.08. The leakage current showed deviation as compared to the curve of previous test results, the test was stopped at 22 kV and 79 microamperes leakage. On April 19 the stepped voltage test on phase C was repeated and stopped at 16 kV with 31.2 microamperes leakage, to prevent imminent insulation breakdown.
Questions:
Will this generator stay operational until a scheduled outage for rewinding?
Should we stop the generator now and proceed with rewinding?
The difference of the costs involved with the decision is quite big, rewinding now being the most expensive.