RRaghunath
Electrical
- Aug 19, 2002
- 1,729
We plan to take the power output of 25MW generator to the 132kV switchyard that is about 2km away for evacuation to the grid.
I would like to know whether we can take the power through OHL directly from the generator transformer 132kV terminals (ofcourse, there will be surge arrestors across the transformer HV windings).
There is space constraint for providing full fledged 132kV switchyard bay with breaker etc. near the transformer.
The 132kV breaker in switchyard (2km away will be controlled from the power plant and there will be trip and interlock circuits will be extended to the switchyard breakers as required by the safety norms / codal requirements.
We can accomodate disconnecting switches, if the same is codal requirement (though I don't think it is).
I would be obliged if some one could tell me the practice / precedences / opinion.
Thanks in anticipation.
I would like to know whether we can take the power through OHL directly from the generator transformer 132kV terminals (ofcourse, there will be surge arrestors across the transformer HV windings).
There is space constraint for providing full fledged 132kV switchyard bay with breaker etc. near the transformer.
The 132kV breaker in switchyard (2km away will be controlled from the power plant and there will be trip and interlock circuits will be extended to the switchyard breakers as required by the safety norms / codal requirements.
We can accomodate disconnecting switches, if the same is codal requirement (though I don't think it is).
I would be obliged if some one could tell me the practice / precedences / opinion.
Thanks in anticipation.