14400:120 PT fuse change

Status
Not open for further replies.

hughboat

Electrical
May 2, 2012
1
silly question from a green horn. anyone familiar with a load break device to pull this fuse hot? or would the common recommendation be to take an outage. this is on a manufacturing facility that would love to avoid an outage.

also, what have you seen as likely causes for PT fuses to blow?

thanks in advance.
 
Replies continue below

Recommended for you

In some kinds of metal clad 15kV switchgear, the PT is mounted in a roll out drawer, which pulls the entire PT+ fuse assembly out.

For outdoor applications I have seen hot stick removal.

What kind of PT and where is it located? Have you made any attempt to determine why the fuse is blowing? I would not want to be the person inserting a fuse into a faulted PT.

See the recent thread on the possible reasons for a blown fuse.
 
Why would you need a load break device to remove a blown fuse? If the fuse is blown there is no load.
 
Strongly recommend against replacing a blown VT fuse with the system energized.

It's impossible to tell if it's a fuse failure or a problem originating from the VT itself. Closing a fuse into a damaged/faulty VT could be dangerous.

Need to check out the VTs prior to trying to re-energize, e.g. megger test, ratio test, and possibly excitation test (if you have comparative results).

 