Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

15 kV clearance issue

Status
Not open for further replies.

tommom

Electrical
Mar 1, 2005
81
I have a contractor who has located a junction box within 4'6" of the front of my switchgear - contrary to the drawings. According to NEC 110.34 (A), condition 2 for 7200 volts to ground, we need 5'0".

What I would like to do is cover or coat the box with insulation to make it Condition 1 for that table, requiring only 4' clearance.

Any ideas? We've considered replacing the box with something 6" shallower, replacing it with a fiberglass box, moving the switchgear, moving the box. None of these can be done.

 
Replies continue below

Recommended for you

The box can be moved. The contractor may not have enough money to make it happen, but the box can be moved.
 
Can you raise it up so it is well above the top of the gear? If it is just a TJB, there is normally little need to access it after it is installed.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor