15kV Cable and Signal Cable

Status
Not open for further replies.

JBUDA54

Electrical
Aug 7, 2001
110
I have a situation on a specific Pocket Vent Project where I will be running a 6" cable tray in close proximity to a 15kV cable tray. What is the minimum distance I have to maintain to stear clear of any induced EM fields that could cause me problems to the 24Vdc 4-20mA cables? Is there a guideline in the code or IEEE Standard? So far I can not find anything. Thanks for your help with this situation. Any comments are greatly welcomed.


 
Replies continue below

Recommended for you

HI JBUDA54
I think 2 ft is recommended [for solid bottom cable tray] according to
IEEE 422-1986
IEEE Guide for Design and Installation of Cable Systems
in Power Generating Stations (ANSI)
Best Regards
 
In addition to using solid bottom tray, a cover might be advisable.
 